National Electrical Code 2014
Chapter 8 Communications Systems
Article 800 Communications Circuits
IV. Grounding Methods
800.100 Cable and Primary Protector Grounding.
(B) Electrode. The grounding conductor shall be connected in accordance with 800.100(B)(1), (B)(2), or (B)(3).
(1) In Buildings or Structures with an Intersystem Bonding Termination. If the building or structure served has an intersystem bonding termination as required by 250.94, the grounding conductor shall be connected to the intersystem bonding termination.
(2) In Buildings or Structures with Grounding Means. If the building or structure served has no intersystem bonding termination, the grounding conductor shall be connected to the nearest accessible location on the following:
(1) The building or structure grounding electrode system as covered in 250.50
(2) The grounded interior metal water piping system, within 1.5 m (5 ft) from its point of entrance to the building, as covered in 250.52
(3) The power service accessible means external to enclosures as covered in 250.94
(4) The nonflexible metallic power service raceway
(5) The service equipment enclosure
(6) The grounding electrode conductor or the grounding electrode conductor metal enclosure
(7) The grounding conductor or the grounding electrode of a building or structure disconnecting means that is grounded to an electrode as covered in 250.32
(3) In Buildings or Structures Without Intersystem Bonding Termination or Grounding Means. If the building or structure served has no intersystem bonding termination or grounding means, as described in 800.100(B)(2), the grounding conductor shall be connected to either of the following:
(1) To any one of the individual electrodes described in 250.52(A)(1), (A)(2), (A)(3), or (A)(4)
(2) If the building or structure served has no intersystem bonding termination or has no grounding means, as described in 800.100(B)(2) or (B)(3)(1), to any one of the individual electrodes described in 250.52(A)(7), and (A)(8) or to a ground rod or pipe not less than 1.5 m (5 ft) in length and 12.7 mm (1/2 in.) in diameter, driven, where practicable, into permanently damp earth and separated from lightning conductors as covered in 800.53 and at least 1.8 m (6 ft) from electrodes of other systems. Steam or hot water pipes or air terminal conductors (lightning-rod conductors) shall not be employed as electrodes for protectors.
800,100 (B) (1)
En Intersystem-bindningsterminering kan antingen vara en uppsättning av terminaler som är säkert monterade och elektriskt anslutna till mätarhöljet, en bindningsstång i närheten av serviceutrustningens hölje eller en bindningsbar nära jordningselektroden. Dessa terminaler är specifikt för bindning och jordning av kommunikationer och andra " intersystem " kretsar.
Om detta existerar, ska telefonen och skålen bindas med dessa terminaler.
800,100 (B) (2)
Om en Intersystem-bindning inte finns finns det en lista över acceptabla alternativ i det här avsnittet. Ingår i listan är " vattenrörsystem för inre metall ". Vilket kan användas så länge som anslutningen ligger inom 5 '(1,5 m) av ingångspunkten, och rören är i direkt kontakt med jorden för 10' (3 m) eller mer (250,52 (A) (1) ).
800,100 (B) (3)
Det här avsnittet ger ännu fler alternativa bindningsställen och pekar igen på 250,52 (A) (1) Metal Underground Water Pipe. .
tl; dr
Anslutning till vattenledningssystemet kan inte vara ett problem, så länge avslutningen ligger inom de första 5 'av röret som kommer in i byggnaden och röret är i direkt kontakt med jorden för 10'. Om emellertid den dielektriska fackföreningen inte är ledande, bör det finnas en lämplig storlek av bindningshoppare som förbinder de två sektionerna av röret.
Om du är orolig för det, eller om du har problem. Du kan flytta bindningsavslutningarna till den andra sidan av den dielektriska facken, använda en alternativ bindningsmetod eller installera en intersystembindningsterminering och använd det.