Jag kör 2 "PVC från mitt hus till ett fristående garage för att köra en 60 amp-matare. Titta på NEC, det verkar som att jag behöver lägga den i SCH 40 under marken. Det verkar dock som om jag måste du använda SCH 80 var som helst, PVC kommer att ligga över marken. Är det rätt, eller kan jag komma undan med SCH 40 för hela körningen?
National Electrical Code 2014
Article 352 - Rigid Polyvinyl Chloride Conduit: Type PVC
II. Installation
352.10 Uses Permitted. The use of PVC conduit shall be permitted in accordance with 352.10(A) through (H).
(F) Exposed. PVC conduit shall be permitted for exposed work. PVC conduit used exposed in areas of physical damage shall be identified for the use.
(G) Underground Installations. For underground installations, homogenous and nonhomogenous PVC shall be permitted for direct burial and underground encased in concrete. See 300.5 and 300.50.
Article 300 - Wiring Methods
I. General Requirements
300.5 Underground Installations.
(D) Protection from Damage. Direct-buried conductors and cables shall be protected from damage in accordance with 300.5(D)(1) through (D)(4).
(4) Enclosure or Raceway Damage. Where the enclosure or raceway is subject to physical damage, the conductors shall be installed in rigid metal conduit, intermediate metal conduit, Schedule 80 PVC conduit, or equivalent.
352.10 (F) säger att PVC-ledningen "som används exponerad i områden med fysisk skada ska identifieras för användning". Jag vet att schema 80 är lämplig för skydd mot fysisk skada, men myndigheten som har behörighet i ditt område kan tillåta schema 40 också. Du kommer att vilja kontrollera med din lokala inspektör, eller använd schema 80 för den exponerade sektionen.
300.5 (D) (4) säger att även om röret är begravd, om det är fysiskt skadat (inte tillräckligt djupt, under en trädgård etc.) måste det fortfarande vara schema 80.
UL 651
Schedule 40, 80, Type EB and A Rigid PVC Conduit and Fittings
1.2 Schedule 40 and 80 conduit and fittings
1.2.1 Schedule 40 rigid PVC conduit and fittings are for aboveground use indoors or outdoors exposed to sunlight and weather, and for underground use by direct burial or encasement in concrete. Schedule 40 rigid PVC conduit, elbows, that are specifically marked for underground use are suitable for use underground only by direct burial or encasement in concrete.
UL-noteringen säger att både 80 och 40 kan användas i både ovan och underjordiska installationer.
Guide Information for Electrical Equipment The White Book 2013
Rigid Nonmetallic PVC Conduit (DZYR)
Use and Installation
Schedule 40 conduit is suitable for underground use by direct burial or encasement in concrete. Schedule 40 conduit marked "Directional Boring""(or "Dir. Boring") is suitable for underground directional boring applications. Schedule 40 conduit is also suitable for aboveground use indoors or outdoors exposed to sunlight and weather where not subject to physical damage. Schedule 40 conduit marked "Underground Use Only" is only suitable for underground applications.
Schedule 80 conduit has a reduced cross-sectional area available for wiring space and is suitable for use wherever Schedule 40 conduit may be used. The marking "Schedule 80 PVC" identifies conduit suitable for use where exposed to physical damage and for installation on poles in accordance with the NEC.
Den vita boken anger tydligt att endast schema 80 är lämpligt för användning där det utsätts för fysisk skada, men återigen säger schema 40 lämplig för jordbruk (om inte annat anges). Så medan du kanske kan använda schema 40 för hela loppet, måste du använda schema 80 genom alla områden där AHJ anser att ledningen utsätts för fysisk skada.