NEC 2011 210.23 Permissible Loads. ... A branch circuit supplying two or more outlets or receptacles shall supply only the loads specified according to its size as specified in 210.23(A) through (D)...
(A) 15- and 20-Ampere Branch Circuits: ...
(1) Cord-and-Plug-Connected Equipment Not Fastened in Place. The rating of anyone cord-and-plug-connected utilization equipment not fastened in place shall not exceed 80 percent of the branch-circuit ampere rating.
(2) Utilization Equipment Fastened in Place. The total rating of utilization equipment fastened in place, other than luminaires, shall not exceed 50 percent of the branch-circuit ampere rating where lighting units, cord-and-plug-connected utilization equipment not fastened in place, or both, are also supplied.
Utnyttjande utrustning är allt som ansluter till nätaggregat.
Du kan ha mer än en installerad enhet på en krets, men om de uppgår till> 50% av den tillgängliga ampaciteten måste kretsen vara dedikerad till dem. I det här fallet installerar en bra installatör en enda (ej duplex) behållare.
Om varmvattenberedaren redan delar en duplexbehållare med din 12A-belastning, måste den antingen vara
- mindre än 4 ampere, eller
- en MWBC. (flertrådsgrenkrets, 2 hots delar en neutral).
Tillverkaren valde sannolikt 12A eftersom 125% av det är 15A, vilket gör den till den perfekta storleken för en 15A-krets. 125% för kontinuerlig belastning. Inte att jag vakuum i> 3 timmar åt gången!