Det är acceptabelt att köra nonmetallic sheathed kabel i ledningen, i själva verket kod kräver det i vissa situationer.
National Electrical Code 2014
Chapter 3 Wiring Methods and Materials
Article 334 Nonmetallic-Sheathed Cable: Types NM, NMC, and NMS
II. Installation
334.15 Exposed Work.
(B) Protection from Physical Damage. Cable shall be protected from physical damage where necessary by rigid metal conduit, intermediate metal conduit, electrical metallic tubing, Schedule 80 PVC conduit, or other approved means...
Räknefyllningsberäkning blir lite svårare vid hantering av kablar, men några noteringar i kapitel 9 ger en viss riktning.
National Electrical Code 2014
Chapter 9 Tables
Notes to Tables
(5) For conductors not included in Chapter 9, such as multiconductor cables and optical fiber cables, the actual dimensions shall be used.
(9) A multiconductor cable or flexible cord of two or more conductors shall be treated as a single conductor for calculating percentage conduit fill area. For cables that have elliptical cross sections, the cross-sectional area calculation shall be based on using the major diameter of the ellipse as a circle diameter.
Not 5 säger att du måste använda kabelns faktiska dimensioner för att bestämma om det passar in i ledningen. Medan not 9 säger att du kan tänka på kabeln som en enda ledare, vilket betyder att om det är det enda i ledningen kan du använda 1-trådfyllnadsprocenten på 53%.
Beräkna området för NM-kabel
Du bör kunna hitta en specifikation från tillverkaren av den kabel du väljer. Jag hittade specifikationen för Southwires Romex® SIMpull®-typ NM-B , som listar storlekarna på olika kablar. Det listar 6/3 kabel som har en diameter på 650 mil, eller 0.650 ". Från vilken du kan beräkna tvärsnittsarean med formeln πr².
(0.650 / 2)^2 * pi =
(0.325)^2 * pi =
0.105625 * pi =
0.3318307240354219108126167073589 in.²
Conduit Fill
När du känner till kabelns område kan du använda Tabell 4 från kapitel 9 i National Electrical Code för att bestämma storleken på ledningen som behövs. Kom ihåg på grund av not 9, kan du använda kolumnen 1 tråd (53%).
Elektrisk metallrör (EMT)
1/2 "@ 53% fylla = 0,161 in.²
3/4 "@ 53% fyll = 0,233 in.²
1 "@ 53% fyll = 0,488 in.²
1/2 "@ 40% fyll = 0.122 in.²
3/4 "@ 40% fyll = 0.213 in.²
1 "@ 40% fyll = 0.346 in.²
Intermediate Metal Conduit (IMC)
1/2 "@ 53% fyll = 0,181 in.²
3/4 "@ 53% fyll = 0.311 in.²
1 "@ 53% fyll = 0,508 in.²
1/2 "@ 40% fyll = 0.137 in.²
3/4 "@ 40% fyll = 0.235 in.²
1 "@ 40% fyll = 0,384 in.²
Rigid Metal Conduit (RMC)
1/2 "@ 53% fyll = 0,166 in.²
3/4 "@ 53% fyll = 0,291 in.²
1 "@ 53% fyll = 0,470 in.²
1/2 "@ 40% fyll = 0.125 in.²
3/4 "@ 40% fyll = 0.220 in.²
1 "@ 40% fyll = 0,355 in.²
Hård PVC-ledning (PVC), Schema 80
1/2 "@ 53% fylla = 0.115 in.²
3/4 "@ 53% fyll = 0.217 in.²
1 "@ 53% fyll = 0.365 in.²
1/2 "@ 40% fyll = 0,087 in.²
3/4 "@ 40% fyll = 0,164 in.²
1 "@ 40% fyll = 0,275 in.²
I det här exemplet behöver du 1 "ledning för att passa den 6/3 nonmetallic sheathed kabeln.
Det andra alternativet. Ska köra 6/3 NM-kabel i källaren och byt sedan till tre 6 AWG THHN-ledare genom ledningen i garaget. Enligt tabell 5 i kapitel 9 i NEC har 6 AWG THHN ett område på 0,0507 in.². Så de tre strömtransportörerna skulle ha en total yta på bara 0,1521 in.².
0.0507 in.² * 3 = 0.1521 in.²
Enligt anmärkning 8 i kapitel 9 kan du använda området som anges i tabell 8 för ledare. Så om du installerar en ledig jordledare i ledningen kan du använda detta värde istället för den isolerade ledarstorleken.
National Electrical Code 2014
Chapter 9 Tables
Notes to Tables
(8) Where bare conductors are permitted by other sections of this Code, the dimensions for bare conductors in Table 8 shall be permitted.
Vilket innebär att du lägger till ytterligare 0,027 in.², för en total summa på 0,171 in.².
0.1521 in.² + 0.027 in.² = 0.1791 in.²
Eftersom det kommer att finnas fler än 2 ledningar i ledningen måste du använda 40% fyllnadsfältet. Även med områdesminskning kan du fortfarande använda 3/4 "kanal istället för 1".