Converting 10 gauge 4-tråd till 10 gauge 3-trådsförsörjning

1

Jag kopplar en dubbel ugn som har en 10 gauge 4-tråds kabel som kommer ut ur en 10 gauge 3-tråds kabel som går till huvudpanelen.

Hur ska jag uppnå detta?

    
uppsättning Steve 29.07.2017 01:35

1 svar

1

Med den nationella elkoden kan en befintlig 3-tråds kabel mata en ny ugn.

Här är den relevanta artikeln från 2014 NEC:

250.140 Frames of Ranges and Clothes Dryers. Frames of electric ranges, wall-mounted ovens, counter-mounted cooking units, clothes dryers, and outlet or junction boxes that are part of the circuit for these appliances shall be connected to the equipment grounding conductor in the manner specified by 250.134 or 250.138.

Exception: For existing branch-circuit installations only where an equipment grounding conductor is not present in the outlet or junction box, the frames of electric ranges, wall-mounted ovens, counter-mounted cooking units, clothes dryers, and outlet or junction boxes that are part of the circuit for these appliances shall be permitted to be connected to the grounded circuit conductor if all the following conditions are met.

(1) The supply circuit is 1201240-volt, single-phase, 3-wire; or 208Y/120-volt derived from a 3-phase, 4-wire, wye-connected system.

(2) The grounded conductor is not smaller than 10 AWG copper or 8 AWG aluminum.

(3) The grounded conductor is insulated, or the grounded conductor is uninsulated and part of a Type SE service-entrance cable and the branch circuit originates at the service equipment.

(4) Grounding contacts receptacles furnished as part of the equipment are bonded to the equipment.

Om alla 1-4 är sanna kan du göra det.

Ugnen ska ha ett bindband från tillverkaren för att låsa neutralen och slipas på ugnen. Och då kan du ansluta både marken och neutralen från ugnen till den neutrala ledningen från 3-tråds kabeln.

Lycka till och vara säker!

    
svaret ges 29.07.2017 11:03