Faktum är att tillhandahålls enheten är UL listad för ändamålet , det finns inga kodproblem involverade. Passande passager är 210,52 (C) (5) (betonar min):
(5) Receptacle Outlet Location. Receptacle outlets shall
be located on or above, but not more than 500 mm (20 in.)
above, the countertop. Receptacle outlet assemblies listed
for the application shall be permitted to be installed in
countertops. Receptacle outlets rendered not readily accessible by appliances fastened in place, appliance garages,
sinks, or rangetops as covered in 210.52(C)(1), Exception,
or appliances occupying dedicated space shall not be considered as these required outlets.
och 406,5 (E):
(E) Receptacles in Countertops and Similar Work Surfaces. Receptacles, unless listed as receptacle assemblies
for countertop applications, shall not be installed in a
face-up position in countertops or similar work surfaces.
Where receptacle assemblies for countertop applications
are required to provide ground-fault circuit-interrupter protection for personnel in accordance with 210.8, such assemblies shall be permitted to be listed as GFCI receptacle
assemblies for countertop applications.
Tyvärr är T & B KPR-15G på "permanent engineering hold", fråga mig inte varför - annars verkar det vara det bästa exemplet där ute av en sådan montering. Om du inte har något emot skillnaden i utseende kan du dock använda Lew PUFP-serien (de dyker upp i en "sidovinkel" jämfört med den vertikala popupen på T & B och Mockett-enheterna, som visas i den här PDF-filen ). Tyvärr visar bilden i frågan Mockett-versionen av detta koncept, som är suck listad som en bärbar strömbrytare, och därför inte kodkompatibel i den här applikationen.