Du kan inte lägga det i en ny struktur i alla fall
Medan regeln om sex (230,71) inte är ett dödbrev (det finns fortfarande fall i nybyggnation där en panel saknar en huvudkoppling kan installeras), så är panelen "delade buss" som du talar om inte längre kodad , eftersom de strider mot 408.36, Undantag 1:
408.36 Overcurrent Protection. In addition to the requirement of 408.30, a panelboard shall be protected by an overcurrent protective device having a rating not greater than that of the panelboard. This overcurrent protective device shall be located within or at any point on the supply side of the panelboard.
Exception No.1: Individual protection shall not be required for a panelboard used as service equipment with multiple disconnecting means in accordance with 230.71. In panelboards protected by three or more main circuit breakers or sets of fuses, the circuit breakers or sets of fuses shall not supply a second bus structure within the same panelboard assembly.
Men marinpaneler är helt olika djur
Marine elektriska redskap är en annorlunda varelse från hushållet saker du tänkte ursprungligen, och lite över det här området i vissa fall. Jag skulle prata med en specialist som är bekant med de subtila riskerna AC på en båt om jag var i dina skor - risker för elstötar är brutala .