Ar den här typen av jordnätanslutning NEC-kompatibel?

3

Hittade det här nyligen, gjort av ett licensierat elföretag i delstaten Kalifornien.

uppsättning Aloysius Defenestrate 07.01.2016 03:12

2 svar

6

Bara vridning räcker inte. Du behöver också en mekanisk anslutning. Trådmutter, krympa, etc.

NEC

110.14 Electrical Connections

Because of different characteristics of dissimilar metals, devices such as pressure terminal or pressure splicing connectors and soldering lugs shall be identified for the material of the conductor and shall be properly installed and used. Conductors of dissimilar metals shall not be intermixed in a terminal or splicing connector where physical contact occurs between dissimilar conductors (such as copper and aluminum, copper and copper-clad aluminum, or aluminum and copper-clad aluminum), unless the device is identified for the purpose and conditions of use. Materials such as solder, fluxes, inhibitors, and compounds, where employed, shall be suitable for the use and shall be of a type that will not adversely affect the conductors, installation, or equipment.

(B) Splices.

Conductors shall be spliced or joined with splicing devices identified for the use or by brazing, welding, or soldering with a fusible metal or alloy. Soldered splices shall first be spliced or joined so as to be mechanically and electrically secure without solder and then be soldered. All splices and joints and the free ends of conductors shall be covered with an insulation equivalent to that of the conductors or with an insulating device identified for the purpose.

Wire connectors or splicing means installed on conductors for direct burial shall be listed for such use.

    
svaret ges 07.01.2016 03:49
-1

NEC-koder 250.148 och 110.14 (B)

Den här typen låser den genom att de bör täckas av någonting. Jag har sett dem utan mindre ledningar, men det är många ledningar för att lita på en bra twist.

    
svaret ges 07.01.2016 03:33