240.24 Location in or on Premises.
(A) Accessibility. Overcurrent devices shall be readily accessible and shall be installed so that the center of the grip of the operating handle of the switch or circuit breaker, when in its highest position, is not more than 2.0 m (6 ft 7 in.) above the floor or working platform, unless one of the following applies:
(1) For busways, as provided in 368.17(C).
(2) For supplementary overcurrent protection, as described in 240.10.
(3) For overcurrent devices, as described in 225.40 and 230.92.
(4) For overcurrent devices adjacent to utilization equipment that they supply, access shall be permitted to be by portable means.
(B) Occupancy. Each occupant shall have ready access to all overcurrent devices protecting the conductors supplying that occupancy, unless otherwise permitted in 240.24(B)(1) and (B)(2).
(1) Service and Feeder Overcurrent Devices. Where electric service and electrical maintenance are provided by the building management and where these are under continuous building management supervision, the service overcurrent devices and feeder overcurrent devices supplying more than one occupancy shall be permitted to be accessible only to authorized management personnel in the following:
(1) Multiple-occupancy buildings
(2) Guest rooms or guest suites
(2) Branch-Circuit Overcurrent Devices. Where electric service and electrical maintenance are provided by the building management and where these are under continuous building management supervision, the branch-circuit overcurrent devices supplying any guest rooms or guest suites without permanent provisions for cooking shall be permitted to be accessible only to authorized management personnel.
(C) Not Exposed to Physical Damage. Overcurrent devices shall be located where they will not be exposed to physical damage.
Informational Note: See 110.11, Deteriorating Agents.
(D) Not in Vicinity of Easily Ignitible Material. Overcurrent devices shall not be located in the vicinity of easily ignitible material, such as in clothes closets.
(E) Not Located in Bathrooms. In dwelling units, dormitories, and guest rooms or guest suites, overcurrent devices, other than supplementary overcurrent protection, shall not be located in bathrooms.
(F) Not Located over Steps. Overcurrent devices shall not be located over steps of a stairway.
Specifikt hindrar 240.24 (D) plats i klädskåp enligt RME.
Om ditt utrymme är dedikerat till andra verktyg, t.ex. Varmvattenberedare, ugn, etc. och du har det nödvändiga godkännandet i enlighet med 110.26 då kan du kalla det en verktygslåda och det finns inom Koden. Många hylla har bara en sådan "garderob".
Det förefaller som om mejeriprodukter inte skulle anses lättantändliga men pappersprodukter skulle vara.
Så, beroende på vad du lagrar i detta skafferi är ditt svar.
Lycka till!